Hy,

I'm now doing my first project with OR, and came across something i can't figure out.
For each light, I defined a an ON and OFF command, and a sensor (STATUS).
Looking at the debug log of knx (/opt/openremote/logs/knx/knx-debug.log) I noticed many "Polling device status" requests.

...
DEBUG 2014-02-02 16:58:46,371 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/101 Data: 0x00
DEBUG 2014-02-02 16:58:46,379 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/109 Data: 0x00
DEBUG 2014-02-02 16:58:46,382 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/111 Data: 0x00
DEBUG 2014-02-02 16:58:46,397 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/2/106 Data: 0x00
DEBUG 2014-02-02 16:58:46,437 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/106 Data: 0x00
DEBUG 2014-02-02 16:58:46,462 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/102 Data: 0x00
DEBUG 2014-02-02 16:58:46,515 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/108 Data: 0x00
DEBUG 2014-02-02 16:58:46,517 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/103 Data: 0x00
DEBUG 2014-02-02 16:58:46,518 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/112 Data: 0x00
DEBUG 2014-02-02 16:58:46,526 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/2/102 Data: 0x00
DEBUG 2014-02-02 16:58:46,537 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/110 Data: 0x00
DEBUG 2014-02-02 16:58:46,540 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/100 Data: 0x00
DEBUG 2014-02-02 16:58:46,542 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/104 Data: 0x00
DEBUG 2014-02-02 16:58:46,544 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/103 Data: 0x00
DEBUG 2014-02-02 16:58:46,582 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/2/102 Data: 0x00
DEBUG 2014-02-02 16:58:46,585 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/105 Data: 0x00
DEBUG 2014-02-02 16:58:46,594 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/100 Data: 0x00
DEBUG 2014-02-02 16:58:46,596 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/111 Data: 0x00
DEBUG 2014-02-02 16:58:46,598 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/0/104 Data: 0x00
DEBUG 2014-02-02 16:58:46,598 (KNX): Polling device status for FRAME L_Data.req 0.0.0 -> 1/1/108 Data: 0x00
...

I was wondering if these many requests aren't overloading the KNX bus?

So i went in ETS and started the bus monitor. The strange thing I noticed is that not all these requests are in the ETS bus monitor, only the group adresses that don't have an actor defined yet. Maybe only not answered read's are monitored?

Is a sensor in OR always active or passive? I defined the status-feedback objects (telegrams) of the switch actuators to be active. Is this correct?

thanks for any help,
Karel

It is a misleading debug statement left over from earlier implementations. So as you noticed, the frames weren't actually reaching the bus. You can ignore the debug output.

Posted by juha at Feb 03, 2014 11:26

Thanks for reply Juha.
This clears things up.

Posted by karelgentens at Feb 08, 2014 07:38